Well as an Electrical Contractor & Chief Electrical Inspector IF you want dead silence what you need to do is isolate your studio circuits from the rest. The only way to do this is have an Electrician run a 50A/220VAC circuit to an isolation transformer and from the trans former to a new panel.Then individual branch circuits as needed from there. The grounding electrode systems is re established at either the transformer or the new panel depending on the wiring configuration and in essence provides you with a new SERVICE that is just for the studio.